Page 1 of 1

LEDs

Posted: 03 Oct 2023, 07:11
by Oleg
LED Control

Controlling LED indicators is a task that's likely at the top of the to-do list for any electronics enthusiast. There's an incredible variety of LEDs available, ranging from the simplest to high-power LEDs and from infrared to ultraviolet.

The illustration showcases an assortment of LEDs with diverse current requirements. Some work perfectly fine with a digital output, while others require transistors or even entire electronic circuits for control.
Variety of LEDs
image.png (106.34 KiB)
Variety of LEDs Viewed 28532 times

Conventional LEDs

Posted: 03 Oct 2023, 07:12
by Oleg
Standard LEDs

Standard LEDs are those familiar, multi-colored 5 mm (sometimes 10 mm or 3 mm) devices that light up with a relatively low current. This makes them suitable for direct control from an Arduino or Raspberry Pi output.

The illustration demonstrates how these LEDs are typically connected to the digital output of an Arduino or Raspberry Pi. A resistor is necessary here to limit the current passing through the LED, and there are two reasons for this: firstly, to avoid exceeding the LED's maximum current rating (otherwise, its lifespan will be short), and secondly, not to exceed the maximum output current on an individual board pin or cumulatively across all of its output pins.
Connecting the LED to the digital output
image.png (35.81 KiB)
Connecting the LED to the digital output Viewed 28531 times

Current limitation

Posted: 03 Oct 2023, 07:20
by Oleg
Understanding LED Direct Voltage and Current

When an LED is connected as shown in the "Connecting an LED to a Digital Input" diagram, the entire circuit will have a more or less constant voltage. This is referred to as the forward voltage of the LED. Depending on the LED's color, the forward voltage can vary; it's typically minimal for red LEDs and highest among all LEDs that emit visible light (see the table).

There are also infrared (IR) LEDs, similar to those found in TV remote controls, and ultraviolet (UV) LEDs, which are often used at parties to give white clothes a violet hue or to check the authenticity of banknotes.

In addition to the forward voltage, another important characteristic of an LED that you need to be aware of is the forward current you intend to pass through it. Most LEDs emit some light with a current as low as 1 mA or slightly less, but they typically reach their optimal brightness at around 20 mA. This is a relatively wide range, so for safety reasons, use a 470 Ohm resistor when working with any LED that you connect to an Arduino or Raspberry Pi, even though the LED may not shine as brightly as it could.

To calculate the resistance of the series resistor conveniently, you can use a special web service that will do the calculations for you. Such a service can be found at led.linear1.org/lled.wiz, and its interface is shown in the diagram below.

As you can see, the calculator assumes a power supply voltage of 3.3 V (obviously, this calculation is for Raspberry Pi), and the maximum current allowed for any Raspberry Pi pin is 16 mA. The calculator suggests that with these parameters, for an LED with a forward voltage of 2.2 V, you should use an 82 Ohm resistor.

If you prefer to perform this calculation manually, start by subtracting the LED's forward voltage value (2.2 V) from the power supply voltage of 3.3 V. This will result in 1.1 V. Then calculate the resistance of the resistor using Ohm's law: R = V / I = 1.1 V / 16 mA = 68.75 Ohms.

When selecting a resistor, you can also refer to the data in the table, which provides approximate forward voltage levels for LEDs of different colors.

Please note: the resistor values have been adjusted and approximated to standard resistor values that are readily available.

Note

In the IR column for the Raspberry Pi device (3.3 V; 3 mA), the symbol 'x' is indicated. Infrared LEDs for remote control devices usually require at least 10 mA to operate, and they are designed with a current rating of 100 mA or more - only at these values do they become sufficiently "long-range."

Online Calculator for Series Resistors
image.png (92.11 KiB)
Online Calculator for Series Resistors Viewed 28530 times
Current-Limiting Resistors for Different LEDs
image.png (47.69 KiB)
Current-Limiting Resistors for Different LEDs Viewed 28530 times

Traffic light

Posted: 03 Oct 2023, 07:28
by Oleg
Creating a Traffic Light with Arduino and Raspberry Pi

With such a fantastic selection of colorful LEDs, let's take red, yellow, and green emitters and create a traffic light controlled by Arduino or Raspberry Pi (see the diagram below).

The LEDs should light up in the following sequence:
1. Red.
2. Red with yellow.
3. Green.
4. Yellow.
Traffic light on Arduino
asd.jpg (68.52 KiB)
Traffic light on Arduino Viewed 28530 times
Components

For this project, you will need the following components to work with Arduino and Raspberry Pi:

- LED1 - Red LED
- LED2 - Yellow LED
- LED3 - Green LED
- R1-3 - 150 Ohm resistors
- A 400-point breadboard
- Male-to-male jumper wires
- Male-to-female jumper wires (for Raspberry Pi only)

Over time, you may start to select resistors with different values, but for this project, I suggest using 150 Ohm resistors for both Arduino and Raspberry Pi, and for LEDs of all three colors. If you want to achieve maximum brightness, consider selecting optimal resistors later on.

Overall Setup

Each of the three LEDs is connected to a separate output pin on Arduino or Raspberry Pi.

Connection to Arduino

The diagram below shows the layout of the breadboard and how it connects to Arduino.

Remember that the longer leads of the LEDs are positive. The LEDs are inserted into the breadboard with these leads on the left, and their ends are connected to their respective resistors. The shorter leads are negative and go from each LED to a row of negative power running along the right edge of the breadboard.
Layout of a breadboard for a traffic light controlled by Arduino
image.png (179.36 KiB)
Layout of a breadboard for a traffic light controlled by Arduino Viewed 28530 times
Arduino Program

Let's go through the sketch:

Code: Select all

const int redPin = 11; // 1 
const int yellowPin = 10;
const int greenPin = 9;

void setup() { // 2
  pinMode(redPin, OUTPUT);
  pinMode(yellowPin, OUTPUT);
  pinMode(greenPin, OUTPUT);
}

void loop() { // 3
  setLEDs(1, 0, 0);
  delay(3000);
  setLEDs(1, 1, 0);
  delay(500);
  setLEDs(0, 0, 1);
  delay(5000);
  setLEDs(0, 1, 0);
  delay(500);
}

void setLEDs(int red, int yellow, int green) {// 4 
  digitalWrite(redPin, red);
  digitalWrite(yellowPin, yellow);
  digitalWrite(greenPin, green);
}

This sketch is quite similar to the original blink sketch, with the difference that we're controlling three LEDs instead of one. Let's break it down using the comments:

1. Constants are defined for each of the Arduino pins connected to the LEDs.
2. In the setup() function, the pins are set as outputs.
3. The loop() function calls the setLEDs() function, which allows turning on or off the three LEDs (setting their values to 1 or 0). The delay before each setLEDs() call determines how long the LED stays in each phase.
4. Thanks to the setLEDs() function, the loop function is simplified, and we can consolidate all three digitalWrite() statements into one line.

PWM and LEDs

Posted: 03 Oct 2023, 07:32
by Oleg
Pulse Width Modulation (PWM) for LED Brightness Control

Attempting to control the brightness of an LED by varying the voltage across it usually does not yield satisfactory results. This is because there is a significant dead zone in the voltage range of the LED, and only after overcoming this zone does the voltage reach a level that allows the LED to emit some light. For controlling LED brightness, analog outputs with PWM (Pulse Width Modulation) work best (see "Pulse Width Modulation" below). LEDs can be turned on and off very quickly, much faster than in a millionth of a second. Using PWM, the LED appears to change brightness proportionally to how long it remains in the on state, although visually, this is perceived as a change in brightness.

Pulse Width Modulation (PWM)

Until now, we've been controlling devices in a very "digital" manner—turning them on and then off. But what if you need to control something more "analog," such as adjusting a motor's speed or an LED's brightness? For this, you need to learn how to control the power supplied to the device.

The technique underlying this kind of control is called Pulse Width Modulation (PWM). It involves using digital outputs that provide a series of high and low pulses. By controlling the fraction of time during which high pulses are applied, you can control the overall power supplied to the motor or LED.

The diagram illustrates how PWM works. It assumes that the voltage at the GPIO (General Purpose Input/Output) pin of the Raspberry Pi is 3.3 V. You will also need a transistor connected to the GPIO pin to provide enough current to control the motor.

The ratio of the pulse duration to its period is called the duty cycle. If the pulses correspond to the on state for only 5% of the entire cycle (duty cycle equals 5%), the motor will receive very little energy, and it will rotate very slowly (or the LED will emit a dim light). Increasing the duty cycle to 50% will provide half the power to the motor or LED, resulting in approximately half the maximum speed or brightness. If the duty cycle increases to 90%, the motor will rotate almost at full speed, and the LED will shine at full intensity.

To turn off the motor or LED, simply reduce the duty cycle to 0, and to achieve full power, raise it to 100%. Maintaining the GPIO pin in a high state continuously will result in a 100% duty cycle.

Both Arduino and Raspberry Pi allow you to use PWM on their output pins. On an Arduino Uno, it can only be enabled on pins D3, D5, D6, D9, D10, and D11—these pins are marked with a tilde (~) on the Arduino board itself. The PWM frequency on Arduino Uno for most pins is 490 Hz (pulses per second). Exceptions are pins 5 and 6, which operate at 980 Hz.

For controlling LED brightness or motor speed, a PWM frequency of 490 Hz, which is the default in Arduino, is perfectly adequate.
Pulse width modulation
image.png (37.05 KiB)
Pulse width modulation Viewed 28530 times

RGB LEDs

Posted: 03 Oct 2023, 07:34
by Oleg
RGB LEDs: Shining a Light on Color Mixing

An RGB LED is a single assembly that actually contains three LEDs: one blue, one red, and one green. By using PWM to control the brightness of each of these LEDs, you can make the RGB LED display any of three colors.

Although an RGB LED contains three regular two-pin LEDs, it doesn't mean the LED package must have six pins. You can connect one pin from each LED together to make it appear as a single pin.

If you connect the negative pins of all LEDs together, the resulting pin is called the common cathode, and if you do the same with the positive pins, you get the common anode.
The scheme of the common cathode of an RGB LED
image.png (31.57 KiB)
The scheme of the common cathode of an RGB LED Viewed 28529 times
RGB LEDs can emit both directional and diffused light. In a directional LED, the red, green, and blue LEDs are clearly distinguishable, and their colors don't mix much. In diffused assemblies, the colors of the three LEDs blend together much better.

Next, we'll be working with displays based on RGB LEDs that have their own control microchip. This chip limits the current to the red, green, and blue LEDs and also serves as a serial data interface. Arduino or Raspberry Pi can control many such LEDs through this interface, using just one output pin.

Re: LEDs

Posted: 03 Oct 2023, 07:38
by Oleg
Experiment: Controlling RGB LEDs with Arduino and Raspberry Pi

In this experiment, we will control the color of an RGB LED using both Arduino and Raspberry Pi. In the version of the experiment performed on Raspberry Pi, we will use a graphical user interface with three sliders to control the color. The images below depict the Raspberry Pi setup and the experiment's schematic.
Connecting a breadboard for mixing colors using aspberry Pi
image.png (255.21 KiB)
Connecting a breadboard for mixing colors using aspberry Pi Viewed 28529 times
The scheme of the experiment with an RGB LED
image.png (66.25 KiB)
The scheme of the experiment with an RGB LED Viewed 28529 times
Components

For this experiment, you will need the following components for both Arduino and Raspberry Pi:

LED1 - RGB LED
R1-3 - 470 Ohm 0.25W resistors
400-point breadboard
Male-to-Male jumper wires
Male-to-Female jumper wires (only for Raspberry Pi)

Please note that Male-to-Female jumper wires are only needed for connecting to the GPIO pins on Raspberry Pi (if you plan to conduct this experiment with Raspberry Pi as well).

To achieve optimal brightness and the best color balance, careful selection of resistors with matching resistances is essential. However, it's easier to obtain the components if you use 470 Ohm resistors for all three channels. They will work with both Raspberry Pi and Arduino.

By the way, the brightness and efficiency of RGB LEDs are such that even at a current of only 3 mA (6 mA for Arduino), the LED will shine quite brightly.

Connection to Arduino

In the Arduino version of this experiment, we use the serial monitor interface to set the proportions of red, green, and blue colors. The diagram below shows the layout of the breadboard and how to connect it to Arduino.
Layout of a breadboard for mixing RGB LED colors using Arduino
image.png (169.76 KiB)
Layout of a breadboard for mixing RGB LED colors using Arduino Viewed 28529 times
The longest lead of the RGB LED is the common cathode, which should be connected to the GND socket on the Arduino board. The order of connecting the other pins may not be the same as shown here, so you may need to rearrange some wires if your colors mix incorrectly.

Arduino Code

The sketch sets up three PWM channels to control the brightness of each of the three colors.

Code: Select all

const int redPin = 11;
const int greenPin = 10;
const int bluePin = 9;

void setup() {
  pinMode(redPin, OUTPUT);
  pinMode(greenPin, OUTPUT);
  pinMode(bluePin, OUTPUT);  
  Serial.begin(9600);
  Serial.println("Enter R G B (E.g., 255 100 200)");
}

void loop() {
  if (Serial.available()) {
    int red = Serial.parseInt();
    int green = Serial.parseInt();
    int blue = Serial.parseInt();
    analogWrite(redPin, red);
    analogWrite(greenPin, green);
    analogWrite(bluePin, blue);
  }
}

Let's clarify some aspects of the sketch using comments:

1. Each of the three PWM values, which should be in the range of 0 to 255, is read into variables.
2. Then, PWM output is set for each channel.

Uploading and Running the Program

After uploading the sketch, open the Serial Monitor window in the Arduino IDE. Then, enter three numbers, each in the range of 0 to 255, separated by spaces, and press the "Send" button. The LED should change color to match the values of red, green, and blue you just entered.

You can individually test each of the channels by entering 255 0 0 (red), 0 255 0 (green), and 0 0 255 (blue).